mmcwick




Joined: 01 Apr 2011
Posts: 3
Location: Berkeley, CA


PostLink    Posted: Fri Apr 01, 2011 10:19 pm    Post subject: 220v Question Reply with quote


        Register to remove this ad. It's free!
I have a basic question about how 220v works: if you disconnect one of the two hot lines to a 220v receptacle, will that receptacle lose all power or will it still be energized at 110v? I assume it losses all power because there is no neutral wire connected to the receptacle, but wanted to confirm this.

Thanks in advance.
Back to top
kal
Forum Administrator



Joined: 12 Dec 2010
Posts: 11120
Location: Ottawa, Canada

Drinking: Pub Ale, Electric Creamsicle, Mild, Pliny the Younger, Belgian Dark Strong, Weizen, Russian Imperial Stout, Black Butte Porter


PostLink    Posted: Sat Apr 02, 2011 12:44 am    Post subject: Reply with quote

I assume you mean 240V.

A typical 240V circuit will have two HOTs and one NEUTRAL.

Across either HOT and a NEUTRAL you have 120V.
Across both HOTs you have 240V.

If you disconnect one HOT, you can still get 120V across the other HOT and NEUTRAL.

For more info, see my page on Supply Power here: http://www.theelectricbrewery.com/control-panel-part-2?page=3

Quote:
In North America, most residential power comes in to the house as 240 Volts AC over 3 wires: Two HOT wires called 'A' and 'B', and a NEUTRAL wire. This power is fed in to your circuit breaker panel which splits it up and feeds it into different circuits throughout the house. The breakers are used to protect the wires in these circuits from overheating. Breakers do not protect the equipment or the people using the equipment.

By connecting (called 'tapping') across different pairs of the three wires we get different voltages:

- 120V AC: By tapping across either of the HOT lines and NEUTRAL for standard household devices such as lights, televisions, computers, etc. Single-pole breakers are used and take up one slot in your breaker panel. Approximately half of the circuit breakers in a house will use HOT 'A', then other half HOT 'B' in order to try and balance out how power is consumed.

- 240V AC: By tapping across the two HOT lines for power hungry devices such as electric stoves, clothes dryers, air conditioning units, baseboard heaters, etc. Double-pole breakers are used and take up two slots in your breaker panel.


Kal

_________________
Our new shop with over 150 new products: shop.TheElectricBrewery.com
We ship worldwide and support our products and customers for life.
Purchasing through our affiliate links helps support our site at no extra cost to you. We thank you!
My basement/bar/brewery build 2.0
Back to top
View user's photo album (21 photos)
mmcwick




Joined: 01 Apr 2011
Posts: 3
Location: Berkeley, CA


PostLink    Posted: Sat Apr 02, 2011 1:37 am    Post subject: Reply with quote

Kal - Thanks for the response. I have read that section a few times and appreciate your explanation.

My original post was based on specific question I had to your wiring diagram for the heating elements. If you close the Power In Relay (via the main key switch) and then close the HLT Relay (via the three-way switch), won't the HOT B line be hot all the way to the HLT receptacle? If that's true and if, for example, the SSR is not supplying power through the HOT A line, will the HLT receptacle and therefore the HLT element be receiving 120v? I'm assuming not, since it would contradict the whole concept of controlling the elements with a PID. I'm looking for an explanation as to why this is. If the HOT B line is not hot at the receptacle in this case, then perhaps I have a fundamental misunderstanding of how the DPDT switches work.

I'm referring to the diagram on this page:
http://theelectricbrewery.com/control-panel-part-2?page=13
Back to top
rosenjm




Joined: 21 Dec 2010
Posts: 249
Location: Ballston Spa, NY


PostLink    Posted: Sat Apr 02, 2011 2:28 am    Post subject: Reply with quote

I'm not really sure I understand what your asking, let's see. If you look at the digram you linked to it appears that only one of the hot lines is "switched" via the SSR. This leaves the other hot live all the time regardless of the SSR position. I assume your question is why the element does not heat up?

When the SSR is "shut" you have 120 V on one side (black) and 120 V on the other side (red) of the element. Each of these lines, or phases is shifted 120 degrees. When you measure from black to red you get 240V (120+120), since the SSR is "shut" you have a path for current to flow, so it does and the element gets hot. With the SSR open you have 120 V on one side (red) and nothing on the other (black), but the SSR is open, so there is no path for current flow so no heat.

In a 120 V circuit, one side (red) is 120 and the other side is ground or neutral at 0 V, giving you 120 V (120+0). Since there is no neutral lead on the element, a single 120V line will not cause them to heat up.

As a side note, when we refer to the line voltage (240 V or 120 V) we are actually talking about the RMS, or root mean square value of the sine wave. The peak voltages are actually higher (0.7 times). If you look at 2 sine waves 120 degrees out of phase, the difference in voltage between them changes constantly. A voltmeter can't respond quickly enough to read those differences, so we take a weighted average, which is about 120V to ground.

Hope that answers your question. Mug
Back to top
View user's photo album (18 photos)
kal
Forum Administrator



Joined: 12 Dec 2010
Posts: 11120
Location: Ottawa, Canada

Drinking: Pub Ale, Electric Creamsicle, Mild, Pliny the Younger, Belgian Dark Strong, Weizen, Russian Imperial Stout, Black Butte Porter


PostLink    Posted: Sat Apr 02, 2011 2:30 am    Post subject: Reply with quote

mmcwick wrote:
Kal - Thanks for the response. I have read that section a few times and appreciate your explanation.

My original post was based on specific question I had to your wiring diagram for the heating elements. If you close the Power In Relay (via the main key switch) and then close the HLT Relay (via the three-way switch), won't the HOT B line be hot all the way to the HLT receptacle?


Yes.

Quote:
If that's true and if, for example, the SSR is not supplying power through the HOT A line, will the HLT receptacle and therefore the HLT element be receiving 120v?


Yes.

Quote:
I'm assuming not, since it would contradict the whole concept of controlling the elements with a PID. I'm looking for an explanation as to why this is. If the HOT B line is not hot at the receptacle in this case, then perhaps I have a fundamental misunderstanding of how the DPDT switches work.


One side of the element is receiving 120V but no current will flow since the circuit is not closed. Think of electricity like water: Until you open the other side (the other HOT line), nothing will flow.

Kal

_________________
Our new shop with over 150 new products: shop.TheElectricBrewery.com
We ship worldwide and support our products and customers for life.
Purchasing through our affiliate links helps support our site at no extra cost to you. We thank you!
My basement/bar/brewery build 2.0
Back to top
View user's photo album (21 photos)
mmcwick




Joined: 01 Apr 2011
Posts: 3
Location: Berkeley, CA


PostLink    Posted: Sat Apr 02, 2011 2:45 am    Post subject: Reply with quote

Thank you both - that's exactly what I needed to know. I'm 90% done with my CP and when reviewing my wiring diagram, had an 'oh sh*t' moment in regards to the HOT B wire going to my element receptacle. Turns out the answer is a fundamental of electricity that I was forgetting. Cheers!
Back to top
Display posts from previous:   
Post new topic   Reply to topic   Printer-friendly view    TheElectricBrewery.com Forum Index -> Building Your Brewery All times are GMT
Page 1 of 1
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum



Forum powered by phpBB © phpBB Group