250amp panel help

 
Post new topic   Reply to topic   Printer-friendly view    TheElectricBrewery.com Forum Index -> Building Your Brewery
View previous topic :: View next topic  
Author Message
rcrabbe13




Joined: 13 Jan 2015
Posts: 2



PostLink    Posted: Tue Jan 13, 2015 10:58 pm    Post subject: 250amp panel help Reply with quote


        Register to remove this ad. It's free!
We are looking at a 250 amp setup with 4 elements and looking for a good starting point. I currently use the 30 amp setup at home, but going to use it in a 7bbl setup at our brewery. Ive seen some threads regarding this but the conversations just stop. And would love to document this for a future sticky thread.

My building has an 800amp service and I have 3 phase 240vac 400amp panel dedicated just for this. I will have a total of 8- 15000 watt elements, but only using them 4 at a time.

What are my options as for parts? Use lighting contactors rated for this type of amp draw or using 4 50a circuits to control each heating element.


Any information would be greatly appreciated.

Cheers.
Back to top
Kevin59




Joined: 03 Aug 2012
Posts: 1047
Location: Fort Collins, CO

Drinking: Imperial Brown Ale

Working on: Oatmeal Stout, IPA


PostLink    Posted: Wed Jan 14, 2015 3:25 pm    Post subject: Reply with quote

First caveat - I'm no expert with 3-phase power...

Now for questions...

Do you know what type of 3-phase power source you have? You've stated 240V 3-phase which would imply a 240V delta configuration. If so is it a 4-wire configuration such that you have both 120V and 240V available?

Are you planning to use 3-phase heating elements? I notice you say 15KW and I know Brewmation sells 3-phase elements but they're rated at 208V.

And if you're planning to use 3-phase elements have you looked into 3-phase GFCI protection? For example:

http://www.bender.org/solutions/gfci.aspx?gclid=CjwKEAiAxNilBRD88r2azcqB2zsSJABy2B96A4gJjjDOPpDBa18IGJ1Xos6Tfrt8f5N8bPF8L9EHLRoCqgHw_wcB

I'm looking for to following this thread and learning more!

Cheers!
Mug

UPDATE: FWIW I'm attaching an Excel spreadsheet I was playing with back when I was considering a startup with electric kettles. Enjoy but no guarantees as to accuracy. I was specifically looking at local utility rates, but also some heating times vs power so you could plug in 60KW.



e_brew_power_v_time_664.xlsx
 Description:

Download
 Filename:  e_brew_power_v_time_664.xlsx
 Filesize:  14.01 KB
 Downloaded:  597 Time(s)

Back to top
View user's photo album (6 photos)
rcrabbe13




Joined: 13 Jan 2015
Posts: 2



PostLink    Posted: Sat Jan 17, 2015 3:10 am    Post subject: Reply with quote

Kevin59 wrote:
First caveat - I'm no expert with 3-phase power...

Now for questions...

Do you know what type of 3-phase power source you have? You've stated 240V 3-phase which would imply a 240V delta configuration. If so is it a 4-wire configuration such that you have both 120V and 240V available?

Are you planning to use 3-phase heating elements? I notice you say 15KW and I know Brewmation sells 3-phase elements but they're rated at 208V.

And if you're planning to use 3-phase elements have you looked into 3-phase GFCI protection? For example:

http://www.bender.org/solutions/gfci.aspx?gclid=CjwKEAiAxNilBRD88r2azcqB2zsSJABy2B96A4gJjjDOPpDBa18IGJ1Xos6Tfrt8f5N8bPF8L9EHLRoCqgHw_wcB

I'm looking for to following this thread and learning more!

Cheers!
Mug

UPDATE: FWIW I'm attaching an Excel spreadsheet I was playing with back when I was considering a startup with electric kettles. Enjoy but no guarantees as to accuracy. I was specifically looking at local utility rates, but also some heating times vs power so you could plug in 60KW.


correct on the 4 wire. I sourced my 3 phase elements from china who have built our tanks. Im not finding much info on the web if I should buy large contacts or just supply 50w elements for each heat stick. Ive been asking breweries around town with limited response but would love to document this for everyone's use. Mug
Back to top
Display posts from previous:   
Post new topic   Reply to topic   Printer-friendly view    TheElectricBrewery.com Forum Index -> Building Your Brewery All times are GMT
Page 1 of 1
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum



Forum powered by phpBB © phpBB Group