Link Posted: Tue Jan 13, 2015 10:58 pm Post subject: 250amp panel help |
|
|
We are looking at a 250 amp setup with 4 elements and looking for a good starting point. I currently use the 30 amp setup at home, but going to use it in a 7bbl setup at our brewery. Ive seen some threads regarding this but the conversations just stop. And would love to document this for a future sticky thread.
My building has an 800amp service and I have 3 phase 240vac 400amp panel dedicated just for this. I will have a total of 8- 15000 watt elements, but only using them 4 at a time.
What are my options as for parts? Use lighting contactors rated for this type of amp draw or using 4 50a circuits to control each heating element.
Any information would be greatly appreciated.
Cheers.
|
|
Back to top |
|
|
Kevin59
Joined: 03 Aug 2012 Posts: 1047 Location: Fort Collins, CO
Drinking: Imperial Brown Ale
Working on: Oatmeal Stout, IPA
|
|
Back to top |
|
|
rcrabbe13
Joined: 13 Jan 2015 Posts: 2
|
Link Posted: Sat Jan 17, 2015 3:10 am Post subject: |
|
|
Kevin59 wrote: | First caveat - I'm no expert with 3-phase power...
Now for questions...
Do you know what type of 3-phase power source you have? You've stated 240V 3-phase which would imply a 240V delta configuration. If so is it a 4-wire configuration such that you have both 120V and 240V available?
Are you planning to use 3-phase heating elements? I notice you say 15KW and I know Brewmation sells 3-phase elements but they're rated at 208V.
And if you're planning to use 3-phase elements have you looked into 3-phase GFCI protection? For example:
http://www.bender.org/solutions/gfci.aspx?gclid=CjwKEAiAxNilBRD88r2azcqB2zsSJABy2B96A4gJjjDOPpDBa18IGJ1Xos6Tfrt8f5N8bPF8L9EHLRoCqgHw_wcB
I'm looking for to following this thread and learning more!
Cheers!
UPDATE: FWIW I'm attaching an Excel spreadsheet I was playing with back when I was considering a startup with electric kettles. Enjoy but no guarantees as to accuracy. I was specifically looking at local utility rates, but also some heating times vs power so you could plug in 60KW. |
correct on the 4 wire. I sourced my 3 phase elements from china who have built our tanks. Im not finding much info on the web if I should buy large contacts or just supply 50w elements for each heat stick. Ive been asking breweries around town with limited response but would love to document this for everyone's use.
|
|