Link Posted: Thu Jan 09, 2020 12:15 am Post subject: 4500W vs. 5500W Boil Time Comparisons |
|
|
My current main electrical panel will only allow a 50 amp sub panel to be placed in my brew space. After looking over the power requirements for the 50amp back to back control panel, my electrician has recommended that I go with (2) 4500w heating elements as (2) 5500w is using just about all the power available and may trip the breaker while in use.
From my understanding, my two options are:
1) Go with (2) 4500W elements and have slower heating times for my boil/HLT, while having back to back batch capability immediately.
2) Go with (2) 5500W elements and have faster heating times, but only use 1 element at a time (either HLT for mash re-circ, or for boiling wort) until I'm able to upgrade my main panel, allowing me to bump my sub-panel up to 70 or 100 amps.
I like the idea of being able to do back to back batches, but I don't see myself doing it as much as doing single, larger batches.
My main concern is how much longer it will take to heat up liquid with a 4500w element. Can anyone provide the time difference for 4500w & 5500w elements for getting 10 and 15 gallon liquids (water/wort) up to mashing and boiling temps?
|
|
Back to top |
|
|
kal Forum Administrator
Joined: 12 Dec 2010 Posts: 11123 Location: Ottawa, Canada
Drinking: Pub Ale, Electric Creamsicle, Mild, Pliny the Younger, Belgian Dark Strong, Weizen, Russian Imperial Stout, Black Butte Porter
|
Link Posted: Thu Jan 09, 2020 1:13 am Post subject: |
|
|
Hi!
I'm not sure why your electrician would be concerned with using two 5500W elements (plus pumps) using either of our 50A panels as we have thousands around the world using this design on a 50A GFI breaker. That is the intended use and allows for a few amps of headroom even with both pumps running.
Our 5500W heating elements will raise the temperature of 1 gallon of water by 1 degree Fahrenheit in approximately 1.6 seconds. A 4500W has 18% less power so it will take approximately 18% longer.
Kal
_________________ Our new shop with over 150 new products: shop.TheElectricBrewery.com
We ship worldwide and support our products and customers for life.
Purchasing through our affiliate links helps support our site at no extra cost to you. We thank you!
My basement/bar/brewery build 2.0
|
|
Back to top |
|
|
JMD887
Joined: 31 Jan 2018 Posts: 120 Location: Akron, Ohio
Drinking: Two Hearted Ale
Working on: American Red IPA
|
Link Posted: Thu Jan 09, 2020 12:40 pm Post subject: |
|
|
Would you have room to run a 60amp GFI breaker set up? To Kal's point- would give more headroom.
|
|
Back to top |
|
|
awoitte
Joined: 19 Jul 2018 Posts: 4
|
Link Posted: Thu Jan 09, 2020 4:23 pm Post subject: |
|
|
JMD887 wrote: | Would you have room to run a 60amp GFI breaker set up? To Kal's point- would give more headroom. |
I wish that were possible, but my panel is being pushed to the limit as it is by running the 50amp breaker. I also talked with a utilities manager at work who said something similar to my electrician, that you typically don't run at or near the max of the power output.
I'm completely going off of the opinions of others as I know nothing about this type of stuff, I just want to make sure everything will perform as expected without hassle while still being safe.
|
|